AlanC2 Posted July 9 Share Posted July 9 The Zone 2 (front) air conditioning in our 2002 Windsor will randomly shut down (without reaching the set temperature) after running for anywhere from 20 minutes to 3.5 hours. Zone 1 has will still have all functions available. Zone 2 in the thermostat, is blank and there are no functions available. I can get it to work again by turning off the master switch at the bottom of the thermostat for a while, then back on. All functions return to zone 2 for a while. Years ago, in the winter, the propane heat for Zone 2 failed and I tracked it down to a bad AC control board in the front unit. At that time, I also replaced the 5 button thermostat with a spare that had come with the motorhome. It's too hot out now to swap out the control boards between the two air conditioning units to test, so I've just ordered a new control board, and a Micro-Air thermostat to replace the old 5 button one in case it's a thermostat problem. When this first happened, we were in a state park with a 30 amp hookup, and I thought maybe as it was a low voltage situation and the EMS kicking in, as I've had that happen before in a state park when the voltage dropped to 90VAC. This time, it also happened twice while running the generator to power zone 2 air conditioning while driving. I have two questions. 1. Since the associated propane furnace won't function with a bad AC power control board in the heat pump unit on the roof, will a bad board in the furnace impact air conditioning operation? 2. Should I be checking something else? Thanks in advance! AlanC2 02 Windsor PST Link to comment Share on other sites More sharing options...
96 EVO Posted July 9 Share Posted July 9 10 minutes ago, AlanC2 said: When this first happened, we were in a state park with a 30 amp hookup, and I thought maybe as it was a low voltage situation and the EMS kicking in, as I've had that happen before in a state park when the voltage dropped to 90VAC. Yikes 😳! Most EMS surge protectors will kill power at about 104V. Link to comment Share on other sites More sharing options...
vito.a Posted July 9 Share Posted July 9 You really need to clean all the RJ11 telephone data cord connections. Start by cleaning the connection in the back of your thermostat. Then drop the inside covers under each A/C unit. Some of the A/Cs will have an RJ11 junction connector. Make sure you clean (and maybe replace) the connections on it as this is most likely your problem spot. I like to use Hosa DeOxit electrical cleaner available on Amazon. It not only cleans the connectors but also deoxidizes and protects the contacts. Hosa D5S-6 CAIG DeoxIT 5% Spray Contact Cleaner, 5 oz Once you have cleaned ALL connections, perform a thermostat reset. Slide the black on/off switch underneath the thermostat to off. While holding down the top and bottom buttons, slide the black switch on. Wait until you see FF in the display and then release the buttons. Hopefully all of your heating and cooling modes will return. Also, I would do this before installing the new thermostat and control board. This will make sure you have a good system before modifying it. 2 Link to comment Share on other sites More sharing options...
AlanC2 Posted July 9 Author Share Posted July 9 16 minutes ago, vito.a said: You really need to clean all the RJ11 telephone data cord connections. Start by cleaning the connection in the back of your thermostat. Then drop the inside covers under each A/C unit. Some of the A/Cs will have an RJ11 junction connector. Make sure you clean (and maybe replace) the connections on it as this is most likely your problem spot. I like to use Hosa DeOxit electrical cleaner available on Amazon. It not only cleans the connectors but also deoxidizes and protects the contacts. https://www.amazon.com/Hosa-D5S-6-DeoxIT-Contact-Cleaner/dp/B00006LVEU?th=1 Once you have cleaned ALL connections, perform a thermostat reset. Slide the black on/off switch underneath the thermostat to off. While holding down the top and bottom buttons, slide the black switch on. Wait until you see FF in the display and then release the buttons. Hopefully all of your heating and cooling modes will return. Also, I would do this before installing the new thermostat and control board. This will make sure you have a good system before modifying it. Thanks for responding, I'm familiar with DeoxIt I forgot to mention that I did hit the RJ11 connections on the back of the thermostat, and on the heat pump unit (accessible from inside) with electrical contact cleaner, working them a few times and also did the hard reset on the thermostat. I did not go up on the roof to access and clean the RJ11 connection on the control board though. The air conditioning shut down after 20 minutes on generator power. It's just too hot here in Maryland to spend a lot of time on the roof, so I will clean the contacts up there when I replace the control board. AlanC2 02 Windsor PST Link to comment Share on other sites More sharing options...
Tom Cherry Posted July 9 Share Posted July 9 Some like BEER. Some like WINE. I do NOT recommend using Detox for a contact cleaner. Plain old Isopropyl Alcohol is safer and works better. Q-Tips are your friend. Vito is RIGHT.... you have a CONNECTION PROBLEM. SO....lets address that and also answer your questions before you start throwing parts at a problem that isn't there. CLEAN THE RJ Connectors....ALCOHOL or PLAIN CRC ELECTRONIC CLEANER. This is SAFER. NOW, if one has used DeTox...and it works....then that is fine. BUT due to the age of these connectors and the brittleness of the plastic and the chemical composition of the plastic, my experience is to use a MILD solvent cleaner and CRC and Alcohol will cause less damaage. I also carry SPARE connectors. Typically, the FRONT AC is Zone 1. IF it reads Zone 2 and it USED to work...then let's not quibble or speculate. Maybe SOMEONE replaced the controller or decided they wanted it to be #2. There is a set of DIP switches on the controller. If NONE of the ZONES are ON or set...the default is Zone 1. SO, where ever your Thermostat is (main galley or hallway), it is "backwards" to how Monaco USUALLY and MAYBE the Windsors were DONE that way. MOVING ALONG. There may be ONE or TWO inline (called Dual Inline Connectors) in the Plenum. There are TWO RJ wires hanging down. There is at least ONE other RJ or maybe 2... Have NO IDEA. You just need to put a piece of tape on the ONES hanging down from the ceiling. They are NOT polarized....they work with EITHER of the other TWO or ONE if you only have ONE. Here is how this nightmare works... THERE might be a POP QUIZ. There is 12 VDC power to EACH AC unit. That is what runs the Control Board. There is a data cable (the lines LOOK with PHONE lines...they are NOT...they have a different RJ termination color code or sequence...a PHONE cable is the same on each end. These are reversed. LIKE 1234 (or the colors) the OTHER end is 4321. DON'T ask for more. You can NEVER substitute or use a PHONE cable. You CAN cut off one END of a Phone Cable and reverse the colors and that is NOW a DATA cable. It won't work on a PHONE.... OK...The PROPER WAY TO START. Pull off the Filter covers. Then locate the two dangling or hanging down RJ's. These are FROM THE CONTROL UNIT. ON the 13.5's they were (maybe) in the plenum. On the 15's they are only accessible from the root after you PULL the cover. They then have the connectors and go to other DATA CABLES.. This is HOW Monaco USED to run them. Thermostat has a data cable. IT runs (TYPICALLY) to the FRONT AC. Then that Thermostat cable is connected to ONE of the hanging ones...the other Hanging ONE then goes to another Data Cable. THAT data Cable goes to the REAR AC. There is NOT another data cable there. This is the END of the line. SO, there will ONLY be ONE connector (Dual Inline). PULL OFF one Dual INLINE at a TIME. Clean the MALE connectors and the FEMALE internal CONTACTS. THEN reconnect. Plug and unplug about 3 times.. FIRMLY push in each time. This cleans the contacts. REPEAT for ALL the Dual INLINE connectors. NOW, you have NOT been doing the PROPER RESET. This is the way it MUST BE DONE. TURN OFF the switch on the bottom of the Thermostat. WAIT about 3 minutes. THEN hold ON or PUSH IN the MODE and ZONE buttons....WHILE THEY ARE HELD IN...THEN turn on the POWER. There will be an FF in the Display. BINGO....you have successfully RESET the System. The thermostat has NOW "TALKED to " or done the HANDSHAKE with the two controller. There is NO 12 VDC line to the Thermostat. There is 12 VDC on TWO of the wires or one "PAIR". NOW....you should have EVERYTHING working. If you lose or can't find a ZONE...or a function as you CYCLE or toggle through the Thermostat. GO BACK AND CLEAN AGAIN. I have replaced my Dual Inline connectors and ALWAYS HAVE SPARES. You have GOT to have a ROBUST or solid connection between the FOUR contact. NEXT UP.. word to the wise. NEVER, again, use the BOTTOM SWITCH. ONLY USE IT TO RESET. TO TURN OFF a ZONE...select the ZONE THEN Toggle through wih the MODE button....to OFF. The switch is mechanical and often fails. SO DON"T abuse it.. NOW...without MORE feedback...IF you have NEVER done the RESET...then you have been LUCKY. You HAVE TO RESET the system (From the Thermostat) every time you break or disconnect one the DATA CABLE connections. They get moisture and dust and vibrate all the TIME. The tiny surface areas get corroded. Replacing the Dual Inline (Amazon has them) is the best way to get it fixed... NOW... the BOARD or the MODULE is erronously named AC CONTROL. YES...it controls the POWER to the Compressor as well as reversing the Valve for HEAT and Cooling. BUT it also has another purpose. Your FURNACE has to have a SIGNAL. Many folks think, and are incorrect, that the Control Board sends "POWER down to the Furnace. WRONG> The two wires (commonly called BLUE) GET NO VOLTAGE or SIGNAL or any "electricity" from the Control Board (Module). There is a RELALY. When the Thermostat, in the HEAT or FURNACE mode, needs HEAT....it signals the Control BOARD. The Furnace or HEAT relay closes. The FURNACE has TWO wires. When the TWO WIRES in the Control Box are JOINTED (Think of the relay as a LIGHT SWITCH), you TURN ON THE SWITCH. When those two wires make a circuit....then the FURNACE starts. There is NO 12 VDC signal. Just the Control Board closing a contact and then the Furnace TAKES over. That's it. Do you have a BAD module? Who KNOWS?? DO the above. THEN test. ODDS ARE (more than 90% of the issues and that is well over 100 members or folks saying...I LOST A ZONE...are in the RJ connections. I had to clean mine THREE times...and I "know how" one time. That is when I ordered NEW connectors...but that was 4 years ago and all is well. GO FIGURE. Thus, we have less than 10 BAD BOARDS or CONTROL Modules. YES, they BREAK. BUT, the issue is in the connection...and if there is the tiniest gap...and it vibrates...the Thermostat "forgets" who's their buddies. In addition, if one never does the RESET...then that will make this happen. Dometic says...RESET every time an RJ cable is disconnected. RESETTING is the FIRST STEP after install. The Thermostat has NO IDEA how many controllers are out there and how they are configured (some with HEAT and some without) and the NAME (zone 1 or 2 or 3. Good Luck. Let us know. I would NOT REPLACE anything until you properly clean and reset, per the Dometic Protocol. Let us know. Link to comment Share on other sites More sharing options...
MyronTruex Posted July 10 Share Posted July 10 Replace the inline couplers as a possible source of issues as well. After cleaning mine a few times and chasing ghosts I just replaced them and tore the old ones apart for inspection. I found corrosion and some questionable connections inside. They live in the updraft area and where I live there is tons of moisture in the air. And at 15 yrs old, they have vibrated constantly and outlived two air conditioners. 1 Link to comment Share on other sites More sharing options...
Solution Dr4Film Posted July 10 Solution Share Posted July 10 The last time I had a similar experience on my 02 Windsor with the rear AC not showing on the 10 Button CCC-2 was because of a bad in-line connector. I tested all of the data lines with my Sperry Instruments cable tester and eventually found the bad in-line connector. Link to comment Share on other sites More sharing options...
AlanC2 Posted July 10 Author Share Posted July 10 18 hours ago, Tom Cherry said: Some like BEER. Some like WINE. I do NOT recommend using Detox for a contact cleaner. Plain old Isopropyl Alcohol is safer and works better. Q-Tips are your friend. Vito is RIGHT.... you have a CONNECTION PROBLEM. SO....lets address that and also answer your questions before you start throwing parts at a problem that isn't there. CLEAN THE RJ Connectors....ALCOHOL or PLAIN CRC ELECTRONIC CLEANER. This is SAFER. NOW, if one has used DeTox...and it works....then that is fine. BUT due to the age of these connectors and the brittleness of the plastic and the chemical composition of the plastic, my experience is to use a MILD solvent cleaner and CRC and Alcohol will cause less damaage. I also carry SPARE connectors. Typically, the FRONT AC is Zone 1. IF it reads Zone 2 and it USED to work...then let's not quibble or speculate. Maybe SOMEONE replaced the controller or decided they wanted it to be #2. There is a set of DIP switches on the controller. If NONE of the ZONES are ON or set...the default is Zone 1. SO, where ever your Thermostat is (main galley or hallway), it is "backwards" to how Monaco USUALLY and MAYBE the Windsors were DONE that way. MOVING ALONG. There may be ONE or TWO inline (called Dual Inline Connectors) in the Plenum. There are TWO RJ wires hanging down. There is at least ONE other RJ or maybe 2... Have NO IDEA. You just need to put a piece of tape on the ONES hanging down from the ceiling. They are NOT polarized....they work with EITHER of the other TWO or ONE if you only have ONE. Here is how this nightmare works... THERE might be a POP QUIZ. There is 12 VDC power to EACH AC unit. That is what runs the Control Board. There is a data cable (the lines LOOK with PHONE lines...they are NOT...they have a different RJ termination color code or sequence...a PHONE cable is the same on each end. These are reversed. LIKE 1234 (or the colors) the OTHER end is 4321. DON'T ask for more. You can NEVER substitute or use a PHONE cable. You CAN cut off one END of a Phone Cable and reverse the colors and that is NOW a DATA cable. It won't work on a PHONE.... OK...The PROPER WAY TO START. Pull off the Filter covers. Then locate the two dangling or hanging down RJ's. These are FROM THE CONTROL UNIT. ON the 13.5's they were (maybe) in the plenum. On the 15's they are only accessible from the root after you PULL the cover. They then have the connectors and go to other DATA CABLES.. This is HOW Monaco USED to run them. Thermostat has a data cable. IT runs (TYPICALLY) to the FRONT AC. Then that Thermostat cable is connected to ONE of the hanging ones...the other Hanging ONE then goes to another Data Cable. THAT data Cable goes to the REAR AC. There is NOT another data cable there. This is the END of the line. SO, there will ONLY be ONE connector (Dual Inline). PULL OFF one Dual INLINE at a TIME. Clean the MALE connectors and the FEMALE internal CONTACTS. THEN reconnect. Plug and unplug about 3 times.. FIRMLY push in each time. This cleans the contacts. REPEAT for ALL the Dual INLINE connectors. NOW, you have NOT been doing the PROPER RESET. This is the way it MUST BE DONE. TURN OFF the switch on the bottom of the Thermostat. WAIT about 3 minutes. THEN hold ON or PUSH IN the MODE and ZONE buttons....WHILE THEY ARE HELD IN...THEN turn on the POWER. There will be an FF in the Display. BINGO....you have successfully RESET the System. The thermostat has NOW "TALKED to " or done the HANDSHAKE with the two controller. There is NO 12 VDC line to the Thermostat. There is 12 VDC on TWO of the wires or one "PAIR". NOW....you should have EVERYTHING working. If you lose or can't find a ZONE...or a function as you CYCLE or toggle through the Thermostat. GO BACK AND CLEAN AGAIN. I have replaced my Dual Inline connectors and ALWAYS HAVE SPARES. You have GOT to have a ROBUST or solid connection between the FOUR contact. NEXT UP.. word to the wise. NEVER, again, use the BOTTOM SWITCH. ONLY USE IT TO RESET. TO TURN OFF a ZONE...select the ZONE THEN Toggle through wih the MODE button....to OFF. The switch is mechanical and often fails. SO DON"T abuse it.. NOW...without MORE feedback...IF you have NEVER done the RESET...then you have been LUCKY. You HAVE TO RESET the system (From the Thermostat) every time you break or disconnect one the DATA CABLE connections. They get moisture and dust and vibrate all the TIME. The tiny surface areas get corroded. Replacing the Dual Inline (Amazon has them) is the best way to get it fixed... NOW... the BOARD or the MODULE is erronously named AC CONTROL. YES...it controls the POWER to the Compressor as well as reversing the Valve for HEAT and Cooling. BUT it also has another purpose. Your FURNACE has to have a SIGNAL. Many folks think, and are incorrect, that the Control Board sends "POWER down to the Furnace. WRONG> The two wires (commonly called BLUE) GET NO VOLTAGE or SIGNAL or any "electricity" from the Control Board (Module). There is a RELALY. When the Thermostat, in the HEAT or FURNACE mode, needs HEAT....it signals the Control BOARD. The Furnace or HEAT relay closes. The FURNACE has TWO wires. When the TWO WIRES in the Control Box are JOINTED (Think of the relay as a LIGHT SWITCH), you TURN ON THE SWITCH. When those two wires make a circuit....then the FURNACE starts. There is NO 12 VDC signal. Just the Control Board closing a contact and then the Furnace TAKES over. That's it. Do you have a BAD module? Who KNOWS?? DO the above. THEN test. ODDS ARE (more than 90% of the issues and that is well over 100 members or folks saying...I LOST A ZONE...are in the RJ connections. I had to clean mine THREE times...and I "know how" one time. That is when I ordered NEW connectors...but that was 4 years ago and all is well. GO FIGURE. Thus, we have less than 10 BAD BOARDS or CONTROL Modules. YES, they BREAK. BUT, the issue is in the connection...and if there is the tiniest gap...and it vibrates...the Thermostat "forgets" who's their buddies. In addition, if one never does the RESET...then that will make this happen. Dometic says...RESET every time an RJ cable is disconnected. RESETTING is the FIRST STEP after install. The Thermostat has NO IDEA how many controllers are out there and how they are configured (some with HEAT and some without) and the NAME (zone 1 or 2 or 3. Good Luck. Let us know. I would NOT REPLACE anything until you properly clean and reset, per the Dometic Protocol. Let us know. Tom, Thanks for the in-depth trouble shooting guide. When this started happening, while we were on a trip a couple of weeks ago, I started searching the "knowledge bank" here and elsewhere for some guidance. Cleaning the RJ11 connections as you described was the first thing I tried, with the exception on the one(s) that connect to the control board up on the roof. I will go back and do that again, check the wires at the plugs, and replace the in-line connectors. If there is a bad plug, I've got spares and a crimper from when I installed a solar system. I misspoke/made an incomplete statement when I mentioned turning the switch at the bottom of the thermostat off and on. I turned it off and on in conjunction with the "reboot" procedure. Other than for rebooting, I don't touch the switch, because of previous warnings about fragility. The reset/reboot is what gets the unit working again after it shuts off. You've answered my question about the furnace board- Thank you! As I mentioned, the heat here in Maryland has been awful. Six o'clock this morning it was 82, and the humidity was 90%, which is too warm for me to go up on the roof. When there is a break, I'll plan on going up before the sun is up and cleaning the contacts on the roof unit. Because of the variability of the shutdowns being between 20 minutes, and three and 3.5 hours, I won't get a chance to really test things until we head out on our next trip at the end of the month. Since I don't want to deal with a failure while we're on a trip with family, I'm planning on also replacing the control board while I'm up there since I already have it. I will be keeping the old one to maybe swap out later. I will advise of success or failure to correct the problem. Thanks again! AlanC2 02 Windsor PST 9 hours ago, MyronTruex said: Replace the inline couplers as a possible source of issues as well. After cleaning mine a few times and chasing ghosts I just replaced them and tore the old ones apart for inspection. I found corrosion and some questionable connections inside. They live in the updraft area and where I live there is tons of moisture in the air. And at 15 yrs old, they have vibrated constantly and outlived two air conditioners. Myron, Thank you for the suggestion! I have new ones on order. AlanC2 02 Windsor PST 7 hours ago, Dr4Film said: The last time I had a similar experience on my 02 Windsor with the rear AC not showing on the 10 Button CCC-2 was because of a bad in-line connector. I tested all of the data lines with my Sperry Instruments cable tester and eventually found the bad in-line connector. Thank you Richard. I'll be going back to reclean connections, check wiring to the plugs/replace plugs if needed, and replace connectors. AlanC2 02 Windsor PST Link to comment Share on other sites More sharing options...
Tom Cherry Posted July 10 Share Posted July 10 1 hour ago, AlanC2 said: Tom, Thanks for the in-depth trouble shooting guide. When this started happening, while we were on a trip a couple of weeks ago, I started searching the "knowledge bank" here and elsewhere for some guidance. Cleaning the RJ11 connections as you described was the first thing I tried, with the exception on the one(s) that connect to the control board up on the roof. I will go back and do that again, check the wires at the plugs, and replace the in-line connectors. If there is a bad plug, I've got spares and a crimper from when I installed a solar system. I misspoke/made an incomplete statement when I mentioned turning the switch at the bottom of the thermostat off and on. I turned it off and on in conjunction with the "reboot" procedure. Other than for rebooting, I don't touch the switch, because of previous warnings about fragility. The reset/reboot is what gets the unit working again after it shuts off. You've answered my question about the furnace board- Thank you! As I mentioned, the heat here in Maryland has been awful. Six o'clock this morning it was 82, and the humidity was 90%, which is too warm for me to go up on the roof. When there is a break, I'll plan on going up before the sun is up and cleaning the contacts on the roof unit. Because of the variability of the shutdowns being between 20 minutes, and three and 3.5 hours, I won't get a chance to really test things until we head out on our next trip at the end of the month. Since I don't want to deal with a failure while we're on a trip with family, I'm planning on also replacing the control board while I'm up there since I already have it. I will be keeping the old one to maybe swap out later. I will advise of success or failure to correct the problem. Thanks again! AlanC2 02 Windsor PST Myron, Thank you for the suggestion! I have new ones on order. AlanC2 02 Windsor PST Alan and I talked. Now understand how his system is configured...and he understands more about the MPX system and the connections and such. He has several "Try this FIRST" options now. Maybe a Data Cable connection...but when we say 90% of them is the cause...the other are in the Board. FWIW, he had a REAR thermostat. Thus his Zone1 is the REAR. That always works. His Front is Zone 2. SO, he will try some things like swapping the "Danglers" up front. and if that doesn't fix it...then odds are...a bad board. BUT if it runs great up there....on both side...then odds are a communications or data cable break between the Front and the Rear. He will be reporting back and posting or calling me. He said THANKS for all the suggestions and comments and now has a much better understanding of the concept. That's it... Link to comment Share on other sites More sharing options...
AlanC2 Posted August 26 Author Share Posted August 26 On 7/10/2024 at 7:17 AM, Dr4Film said: The last time I had a similar experience on my 02 Windsor with the rear AC not showing on the 10 Button CCC-2 was because of a bad in-line connector. I tested all of the data lines with my Sperry Instruments cable tester and eventually found the bad in-line connector. Apologies for taking so long to post this. I was delayed by a surgery, and I wanted to test the system during a trip to make sure the repair worked. I also want to thank Tom Cherry for all of the assistance he gave. Since I was going to go on a trip after my surgery, and did not want to deal with this issue on the road, I took the shotgun approach. I cleaned all of the RJ11 connectors, and since I had to go up on the roof to complete that task, I replaced the "control" board in the front air conditioning unit. I also replaced the 5 button thermostat with a Micro-Aire thermostat as I couldn't find a new 5 button unit. After doing that I ran the unit and then flicked the RJ11 couplers in the front and rear units, that can be accessed inside the motorhome, with my finger. The coupler for the data cable in the rear turned out to be bad. There are two couplers in the rear unit on the 02 Windsor PST, and this is what drove Tom and I crazy. There are "straight thru" RJ11 couplers, and there are "reverse" RJ11 connectors, and believe it or not, there is a lot of bad info on the internet about terminology and which is which. If you replace one of the couplers in the rear unit with the incorrectly wired coupler, neither air conditioner will work. I tested the existing couplers with a continuity tester and knew what I needed connection wise. After getting the wrong couplers from Amazon, and one other company, Tom found L-Com. The correct coupler is their TDG1026-4R. As long as the wire map is the same, you obviously can use anyone's coupler. I ran the air conditioning constantly during the entire 3 week long trip, and not once was there a problem. Thanks again to all for their input, and especially to Tom Cherry. AlanC2 02 Windsor PST Link to comment Share on other sites More sharing options...
relipp Posted Saturday at 11:27 PM Share Posted Saturday at 11:27 PM my control panel in front ac is bad where can I get it rebuild 2000 dynasty with 12000 do therm Link to comment Share on other sites More sharing options...
Tom Cherry Posted Sunday at 01:46 AM Share Posted Sunday at 01:46 AM 2 hours ago, relipp said: my control panel in front ac is bad where can I get it rebuild 2000 dynasty with 12000 do therm Does Lippert not have a part number or a new one? they were fairly common. They are called the AC BOARD. They, I THINK, worked with the original 4 button and later 5 button they were all CCC MPX Link to comment Share on other sites More sharing options...
Dr4Film Posted Sunday at 11:10 AM Share Posted Sunday at 11:10 AM 11 hours ago, relipp said: my control panel in front ac is bad where can I get it rebuild 2000 dynasty with 12000 do therm Did you check eBay??? There are some listed but there is one in particular that will repair older Dometic 4 and 5 Button Thermostats. https://www.ebay.com/sch/i.html?_from=R40&_trksid=p3519243.m570.l1313&_nkw=Dometic+5+Button+Thermostat+repair&_sacat=0 Link to comment Share on other sites More sharing options...
Tom Cherry Posted Sunday at 01:26 PM Share Posted Sunday at 01:26 PM 15 hours ago, Dr4Film said: Did you check eBay??? There are some listed but there is one in particular that will repair older Dometic 4 and 5 Button Thermostats. https://www.ebay.com/sch/i.html?_from=R40&_trksid=p3519243.m570.l1313&_nkw=Dometic+5+Button+Thermostat+repair&_sacat=0 The above is for the THERMOSTATS. Based on the POST...I THINK the issue is the Control Module or the AC Board (Dometic's Part Description). To best of my knowledge, there are NO "Tech" or services that will repair the boards. You buy a new one. The boards should be PLUG and play in that the harnesses are the same. I would call Lippert. You need to have the MODEL and SN of the front (12K?) unit. Ask them for the replacement number. They can ALSO give you the OLD Part Number of the AC Board. Then you GOOGLE that. Lippert should tell you if a new or the current CCC (not the NEW Penguin II CCC2 System) will work. Start there....get the fact and info. It should work out.... BTW. I pulled your Sales Brochure. Your STOCK or FACTORY configuration was the 13.5 K AC/HP units. Those SHOULD have the same AC Board (Control Module) and the current part number is 3312022. Again Lippert Tech Support will verify that. Here is a link to one on Amazon...but check the PN. Dometic 3312022 Duo Therm Electronic Board Link to comment Share on other sites More sharing options...
TomV48 Posted Tuesday at 05:51 AM Share Posted Tuesday at 05:51 AM On 7/9/2024 at 12:46 PM, AlanC2 said: The Zone 2 (front) air conditioning in our 2002 Windsor will randomly shut down (without reaching the set temperature) after running for anywhere from 20 minutes to 3.5 hours. Zone 1 has will still have all functions available. Zone 2 in the thermostat, is blank and there are no functions available. I can get it to work again by turning off the master switch at the bottom of the thermostat for a while, then back on. All functions return to zone 2 for a while. Years ago, in the winter, the propane heat for Zone 2 failed and I tracked it down to a bad AC control board in the front unit. At that time, I also replaced the 5 button thermostat with a spare that had come with the motorhome. It's too hot out now to swap out the control boards between the two air conditioning units to test, so I've just ordered a new control board, and a Micro-Air thermostat to replace the old 5 button one in case it's a thermostat problem. When this first happened, we were in a state park with a 30 amp hookup, and I thought maybe as it was a low voltage situation and the EMS kicking in, as I've had that happen before in a state park when the voltage dropped to 90VAC. This time, it also happened twice while running the generator to power zone 2 air conditioning while driving. I have two questions. 1. Since the associated propane furnace won't function with a bad AC power control board in the heat pump unit on the roof, will a bad board in the furnace impact air conditioning operation? 2. Should I be checking something else? Thanks in advance! AlanC2 02 Windsor PST Everybody wants to get all technical about these kinds of things but our bedroom AC was cutting out randomly. Along with cleaning the coils externally, I opened the fan vent above my head and found that the insulators and baffles had moved around so that it was recirculating air internally without circulating it out in to the room. This was causing the unit to shut down; causing the unit to freeze up; and was causing the unit to drip water on me in my sleep at night. We clean the coils on the outside and straightened out the baffling on the inside and that thing is unlike new. Incorrect air circulation is apparently hard on the whole system Link to comment Share on other sites More sharing options...